Princeton,IN | Showing 17.5 WHAT? I wouldn't assume that the demand didn't record starting AC/Heat units or other things that might have a high starting demand. I would assume it DID, that's what it is there for. If you have a 200 amp main breaker, 25KVA will carry it. 25,000 (volts x amps) / 240volts = 104.1667 amps on each leg. If your power company delivers 220volts: 25,000/220 =113.6363 amps on each leg. now, if you have a 400 amp service to your house, double it. And,by the way, did you know those main breakers are only going to carry 80% of there name plate rating. Thus, your utility installs a "320" meter in your 400 amp service. Now, if your house is feeding the shop, go add the shop main breaker into your calculations.
|