It's 2005 817 Fendt the valve was installed in 2007 when we steered with Insight and trimble NAV stuff.
Only problem we have had was replace 1 coil because wires broke at the coil.
So, are you using the CAN valve on the FENDT tractor, or a Trimble valve installed in 2007?
Because if you are using the factory FENDT valve that hasn't been used since 2007 then you have absolutely zero idea if it is functioning, or was every calibrated from the dealer in 2005.
So, if you are trying to use the CAN valve, get your dealer to calibrate the factory valve first. If still no communication, valve is likely bad.